    I almost always work with pure 120V AC equipment, but now with the new
    6500 equipment I am getting, I am little confused about something.

    In a house, you have two 120V supply lines of the same phase. In your
    breaker panel, you can install a breaker which grabs voltage from each
    bus, and you wire a standard 240V device - like a dryer or AC unit,
    etc.,.

    Here is where I get confused. Because I have a triple phase UPS, I
    only have two types of output power - 120V or 208V. I actually have
    three 120V phase, and none of them are of the same phase. So its
    impossible for me to wire the 240V equipment like I would at home.
    However, I have the 208V power.

    Is it safe to assume that any 240V appliance can run off 208V? Cisco's
    power spec for the 6500 just says anything between 100V and 250V. Can
    someone clarify this for me. I just want to be sure I am correct in
    assuming that 208V and 240V are the same. Obviously the wiring is
    different. 240V is 4 wires (120V supply, 120V supply, return, and
    ground), and 208V has 3 wires (208V supply, return, and ground)....

    thanks
    john
    essenz, Jun 5, 2007
    #1
    1. Advertising

  2. essenz <> writes:
    >I almost always work with pure 120V AC equipment, but now with the new
    >6500 equipment I am getting, I am little confused about something.


    >In a house, you have two 120V supply lines of the same phase. In your
    >breaker panel, you can install a breaker which grabs voltage from each
    >bus, and you wire a standard 240V device - like a dryer or AC unit,
    >etc.,.


    Right. In residential neighborhoods, you end up with two legs in phase,
    but opposite voltages coming into your house, center tapped. So the
    difference between your two 120V legs is 240V.


    >Here is where I get confused. Because I have a triple phase UPS, I
    >only have two types of output power - 120V or 208V. I actually have
    >three 120V phase, and none of them are of the same phase. So its
    >impossible for me to wire the 240V equipment like I would at home.
    >However, I have the 208V power.


    Right Three phase vs. single phase.
    Just dealing with 120V off your 3-phase UPS you get 120V. But, when you
    take two legs of the three, you get things 120degrees out of phase
    between the two, so by the time one leg is leading, the other is
    falling. RMS difference between two legs ends up being 208V
    between the two legs because of the phase difference once you work out
    the math.


    >Is it safe to assume that any 240V appliance can run off 208V? Cisco's
    >power spec for the 6500 just says anything between 100V and 250V. Can
    >someone clarify this for me. I just want to be sure I am correct in
    >assuming that 208V and 240V are the same. Obviously the wiring is
    >different. 240V is 4 wires (120V supply, 120V supply, return, and
    >ground), and 208V has 3 wires (208V supply, return, and ground)....


    You have to be careful of what you define as a 240V appliance.
    A 240V dryer or heater might not operate quite right on 208V...

    But, something like a 6500 is designed to operate just fine on 208V,
    because that is the expected environment it will be going into. Note:
    Most computer gear runs just fine off 120V or 208V power or 220/230/240V
    power, as the power supplies are all auto-sensing for the voltage
    level for all areas around the world, and adjusts appropriately. That
    way, manufacturers can just ship the correct power plug for the region
    and not have seperate power supplies trying to figure out what power
    is what in what area of the world it ships to.

    You also have to be mindful of *what* power supplies you put into your
    6500. Some are 120V/208V. Some higher-wattage ones are 208V only, to
    stay within your current ratings (ie. they'll be 208Vx16A feeds, which
    is going to be more current than most wire run for 120V will take, but
    works just fine for 208V).

    You aren't quite right on the wiring though.

    240V residential is normally run with 12-3 NM cable in the house.
    Two phases of power, neutral and ground. It doesn't run in EMT or BX
    conduit like some areas used to have many years ago.

    BUT, 208V commercial is normally run with 3 THHN inside EMT conduit.
    You still have two phases, and one neutral, but the ground run is the EMT
    conduit itself. The ground will be tied to the neutral at one point, probably
    the main PDU for your UPS, which is then grounded to the building ground.

    My house is old enough that all oldwork is run in EMT or BX, which was
    the designed in ground for the 2 THHN conductors they pulled in each,
    so my home wiring is more like commercial environments. But
    residential is all done with NM cable now which is cheaper and quicker
    to run.

    So, ultimately, your 6500 power supplies are designed to work on the
    208V feed your 3-phase UPS will generate for it, and you don't have to
    worry about it.
    Doug McIntyre, Jun 5, 2007
    #2
    1. Advertising

Want to reply to this thread or ask your own question?

It takes just 2 minutes to sign up (and it's free!). Just click the sign up button to choose a username and then you can ask your own questions on the forum.
Similar Threads
  1. Replies:
    3
    Views:
    533
    Leonidas Jones
    Jan 21, 2005
  2. Replies:
    6
    Views:
    519
    Leonidas Jones
    Mar 26, 2005
  3. Hans
    Replies:
    2
    Views:
    455
  4. Roger Barbeau

    70-240

    Roger Barbeau, Mar 1, 2004, in forum: MCSE
    Replies:
    4
    Views:
    693
    Roger Barbeau
    Mar 5, 2004
  5. Katy Patooty

    Passed 70-240

    Katy Patooty, Jul 17, 2004, in forum: MCSE
    Replies:
    20
    Views:
    958
    catwalker63
    Jul 20, 2004
Loading...

Share This Page